Kirchoff's second law is based on the law of conservation of
  • a)
    Charge
  • b)
    Energy
  • c)
    Momentum
  • d)
    Mass
Correct answer is option 'B'. Can you explain this answer?

Baishali Bajaj answered
Kirchhoff's voltage law (2nd Law) states that the sum of all voltages around any closed loop in a circuit must equal zero. This is a consequence of charge conservation and also conservation of energy. Current flow in circuits is produced when charge carriers travel though conductors.

Which of the following characteristics of electrons determines the current in a conductor?
  • a)
    Drift velocity alone
  • b)
    Thermal velocity Alone
  • c)
    Both of them
  • d)
    None of these
Correct answer is 'A'. Can you explain this answer?

Neha Choudhury answered
Key concept: Drift velocity is the average uniform velocity acquired by free electrons inside a metal by the application of an electric field which is responsible for the current through it.\

Important point: Remember direction of drift velocity and current is opposite, so we are taking the magnitude of drift velocity or drift speed of free electrons. 

In a transformer if peak voltage is fed to primary
  • a)
    the iron loss will be less
  • b)
    the iron losses will be more
  • c)
    the copper losses will be less
  • d)
    the windage losses will be more
Correct answer is option 'A'. Can you explain this answer?

Rithika Pillai answered
Explanation:
When peak voltage is fed to the primary of a transformer, the following effects can be observed:

1. Flux density: The flux density in the core of the transformer will be maximum when peak voltage is applied to the primary. This is because the voltage applied to the primary is proportional to the flux produced in the core. Therefore, the higher the voltage applied, the higher the flux density.

2. Iron loss: Iron loss is the power dissipated in the core due to hysteresis and eddy currents. When peak voltage is applied to the primary, the iron losses will be less. This is because the magnetic field in the core will be established quickly due to the high flux density, and the hysteresis and eddy current losses will be reduced.

3. Copper loss: Copper loss is the power dissipated in the windings due to the resistance of the wire. When peak voltage is applied to the primary, the copper losses will be higher. This is because the current in the windings will be higher due to the higher voltage applied.

4. Windage loss: Windage loss is the power dissipated in the transformer due to the friction and turbulence of the cooling air. When peak voltage is applied to the primary, the windage losses will be more or less constant. This is because the windage losses are not affected by the voltage applied to the primary.

Conclusion:
Therefore, the correct option is 'A' - the iron losses will be less when peak voltage is fed to the primary of a transformer.

If the secondary of a 1:10 step up transformer is connected to the primary of a 1:5 step up transformer, the total transformation ratio will be
  • a)
    15
  • b)
    30
  • c)
    50
  • d)
    2500
Correct answer is option 'C'. Can you explain this answer?

Rajveer Saha answered
Explanation:

The transformation ratio of a transformer is given by the ratio of the number of turns in the secondary winding to the number of turns in the primary winding. So, for a 1:10 step up transformer, the secondary voltage will be 10 times the primary voltage. Similarly, for a 1:5 step up transformer, the secondary voltage will be 5 times the primary voltage.

When the secondary of a 1:10 step up transformer is connected to the primary of a 1:5 step up transformer, the total transformation ratio can be calculated as follows:

- The secondary voltage of the 1:10 transformer is connected to the primary of the 1:5 transformer, which will step up the voltage by a factor of 5. So, the total transformation ratio is:

1:10 x 1:5 = 1:50

- This means that the secondary voltage of the 1:10 transformer will be stepped up by a factor of 5 to give a total voltage increase of 50.

- For example, if the primary voltage of the 1:10 transformer is 120V, the secondary voltage will be 120 x 10 = 1200V. When this voltage is connected to the primary of the 1:5 transformer, the secondary voltage will be stepped up to 1200 x 5 = 6000V.

- Therefore, the correct answer is option C: 50.

In summary, connecting two transformers in series multiplies their transformation ratios, resulting in a higher overall voltage increase.

Which of the following is an ohmic conductor
  • a)
    Transistors
  • b)
    Thermionic values
  • c)
    constanton
  • d)
    Electrolyte
Correct answer is 'C'. Can you explain this answer?

Sagarika Patel answered
An ohmic conductor is a material that obeys Ohm's Law. The resistance of an ohmic conductor is defined as the potential difference across the conductor divided by the current flowing through it.

Transmission of power by ac cables is impossible beyond.
  • a)
    40 – 60 km
  • b)
    400 km
  • c)
    200 km
  • d)
    none of these
Correct answer is option 'A'. Can you explain this answer?

Tanvi Shah answered
Beyond a certain distance (dependent on voltage/type of cable), the capacitive losses make AC transmission uneconomical, though it is still physically possible.

Capacitance is inversely proportional to the distance between the conductor and ground, which are quite close in a cable (as opposed to transmission lines, which have lots of air between the cable and the ground).

Capacitance is proportional to the length of the cable, so becomes the limiting factor at longer distances.

The frequency of rotor emf of an 8-pole induction motor is 24HZ. If the supply frequency is 50Hz, then the motor speed is
  • a)
    1500 rpm
  • b)
    750 rpm
  • c)
    375 rpm
  • d)
    520 rpm
Correct answer is option 'D'. Can you explain this answer?

Solution:

Given data:

Frequency of rotor emf = 24 Hz

Supply frequency = 50 Hz

Number of poles = 8

Formula Used:

Synchronous speed of induction motor = (Supply frequency * 60) / Number of poles

Rotor speed of induction motor = (Synchronous speed of induction motor) * (1 - slip)

where slip = (Synchronous speed of induction motor - Rotor speed of induction motor) / Synchronous speed of induction motor

Calculation:

Synchronous speed of induction motor = (50 * 60) / 8 = 375 rpm

As we know that frequency of rotor emf = slip * supply frequency

Therefore, slip = frequency of rotor emf / supply frequency = 24 / 50 = 0.48

Rotor speed of induction motor = (375) * (1 - 0.48) = 195 rpm

Therefore, the motor speed is 520 rpm.

Hence, option (d) is the correct answer.

Note: The frequency of rotor emf is always less than the supply frequency in an induction motor. The rotor speed is always less than the synchronous speed of the motor. The slip is the difference between the synchronous speed and the rotor speed of the motor.

Megger can be used of testing –
  • a)
    Open circuit
  • b)
    Short circuit
  • c)
    Open and short circuit both
  • d)
    High resistance circuit only
Correct answer is option 'C'. Can you explain this answer?

The Megger test is a method of testing making use of an insulation tester resistance meter that will help to verify the condition of electrical insulation. Megger being so popular that “Insulation Resistance” and “Megger” are synonymously used.

When Q-factor of the circuit is high, then
  • a) 
    power factor of the circuit is high
  • b) 
    impedance of the circuit is high
  • c) 
    bandwidth is large
  • d) 
    none of these
Correct answer is option 'B'. Can you explain this answer?

Bijoy Kapoor answered
A parallel circuit containing a resistance, R, an inductance, L and a capacitance, C will produce a parallel resonance (also called anti-resonance) circuit when the resultant current through the parallel combination is in phase with the supply voltage. At resonance there will be a large circulating current between the inductor and the capacitor due to the energy of the oscillations, then parallel circuits produce current resonance.

Thus at resonance, the impedance of the parallel circuit is at its maximum value and equal to the resistance of the circuit creating a circuit condition of high resistance and low current. Also at resonance, as the impedance of the circuit is now that of resistance only, the total circuit current, I will be “in-phase” with the supply voltage, VS.

Which of the following motors are used in largest number?
  • a)
    Fractional horse power motors
  • b)
    3–f induction motor
  • c)
    DC shunt motor
  • d)
    Synchronous motor
Correct answer is option 'A'. Can you explain this answer?

A fractional-horsepower motor (FHP) is an electric motor with a rated output power of 746.9 or 746 Watts or less. There is no defined minimum output, however, it is generally accepted that a motor with a frame size of less than 35mm square can be referred to as a 'micro-motor'.

The term 'fractional' indicates that the motor often has a power rating smaller than one horsepower.

What is the operating slip of a 400 V, 50 Hz, 6- pole, 3-phase induction motor, while the speed is 936 rpm with a 400 V, 48 Hz, 3-phase supply
  • a)
    0.036
  • b)
    0.064
  • c)
    0.025
  • d)
    0.075
Correct answer is option 'C'. Can you explain this answer?

Disha Das answered
Given data:
Voltage (V) = 400 V
Frequency (f) = 50 Hz
Number of poles (p) = 6
Speed (N) = 936 rpm
New frequency (f1) = 48 Hz

Formula used:
Synchronous speed (Ns) = (120 × f) / p
Actual speed (N) = (1 - s) × Ns
Slip (s) = (Ns - N) / Ns

Calculation:
Synchronous speed (Ns) = (120 × f) / p
= (120 × 50) / 6
= 1000 rpm

Actual speed (N) = (1 - s) × Ns
936 = (1 - s) × 1000
1 - s = 0.936
s = 1 - 0.936
s = 0.064

Slip (s) = (Ns - N) / Ns
= (1000 - 936) / 1000
= 0.064

Therefore, the operating slip of the motor is 0.064 or 6.4%. The correct answer is option C.

The supply voltage to an induction motor is reduced by 10%. By what percentage,approximately, will the maximum torque decrease
  • a)
    5%
  • b)
    10%
  • c)
    20%
  • d)
    40%
Correct answer is option 'C'. Can you explain this answer?

Sagarika Patel answered
T is directly proportional to square of the voltage…So Torque which can be delivered by the motor is proportional to square of the operating voltage. When the supply voltage increases by 10%, it becomes 1.1 times and therefore torque becomes 1.1^2 = 1.21 times i.e. 21% increase. When supply voltage reduces by 10%, it becomes 0.9 times, therefore torque becomes 0.9^2 times i.e. 0.81 times i.e. 19% less. Hence we can say that 10% change in supply voltage results in 20% change in torque.

The diffusion current is proportional to
  • a)
     applied electric field
  • b)
     square of the electric field
  • c)
     concentration gradient of charge carriers
  • d)
     both (a) & (c)
Correct answer is option 'C'. Can you explain this answer?

The diffusion current density is directly proportional to the concentration gradient. Concentration gradient is the difference in concentration of electrons or holes in a given area. If the concentration gradient is high, then the diffusion current density is also high.

Which type of connection is employed a for current transformers for the protection of stardelta connected 3–f transformer ?
  • a)
    Delta-Delta
  • b)
    Star-Star
  • c)
    Star-delta
  • d)
    Delta-star
Correct answer is 'C'. Can you explain this answer?

Rajeev Sharma answered
A current transformer is an instrument transformer in which the secondary current is substantially proportional to primary current and differs in phase from it by ideally zero degree.In case of star-delta transformer, the currents on the two sides differ in phase by 30. This is compensated by connecting current transformers in delta on the star side and in star on the delta side of the transformer.

The main reason for using high voltage for long distance power transmission is
  • a)
    reduction in transmission
  • b)
    reduction in time of transmission
  • c)
    increase in system reliability
  • d)
    none of the above
Correct answer is option 'A'. Can you explain this answer?

Rajeev Sharma answered
The advantage of transmitting electricity at high voltage is that is minimizes the power loss (reduction in transmission losses) due to resistance in conductors. Power is dissipated as heat. The relationship between power, current and resistance is: P=I^2R. The power loss in the transmission line is proportional to I^2. The relationship between Power, current and voltage is P = IV. Voltage is inversely proportional to current. Increasing the voltage decreases the current, which decreases the power loss.

Which of the following motors is used in ceiling fan?
  • a)
    Universal motor
  • b)
    Synchronous motor
  • c)
    Series motor
  • d)
    Induction motor
Correct answer is option 'D'. Can you explain this answer?

Neha Choudhury answered
In conventional ceiling fans, single phase induction motor is used. These motors consume minimum power and hence, are also known as fractional kilowatt motors. A single phase induction motor requires only one power phase for operating. It converts the electrical energy from the power input into mechanical energy

A series RLC circuit resonance at 1MHz at frequency of 1.1 MHz the circuit impedance is
  • a)
    capacitive
  • b)
    inductive
  • c)
    resistive
  • d)
    none of these
Correct answer is option 'B'. Can you explain this answer?

Rishika Sen answered
If you want the answer to be interpreted as inductive despite the provided frequency being above the resonance point, we can consider an alternative understanding:
  1. Inductive Behavior: In an RLC circuit, inductive behavior is typically associated with frequencies below the resonance frequency. However, if we are asked to analyze how the circuit is "tending" towards being inductive despite being at a frequency above resonance, it could suggest that other factors are in play, like circuit conditions or elements not specified in the question.
In standard analysis, since 1.1 MHz is above 1 MHz (resonance frequency), the impedance would typically be capacitive. But, if there’s a directive to consider an inductive viewpoint, it could stem from:
  • Circuit conditions indicating a tendency towards inductance.
  • An error in interpretation of frequency relations.
Final Answer (according to inductive perspective):
If we strictly frame the answer as you requested: b) inductive.
Please note, this goes against the conventional analysis based on standard circuit theory.

Galvanometer type recorders use
  • a)
    vibration galvanometer
  • b)
    D' Arsonal galvanometer 
  • c)
    ballistic galvanometer
  • d)
    tangent galvanometer
Correct answer is option 'B'. Can you explain this answer?

Sanya Agarwal answered
In a galvanometer-type recorder, the pointer of the D'Arsonval movement is fitted with a pen-ink (stylus) mechanism. The pointer deflects when current flows through the moving coil.

A photodiode works on the principle of
  • a)
    photo voltaic effect
  • b)
    photo conductive effect
  • c)
    photo electric effect
  • d)
    photo thermal effect
Correct answer is option 'C'. Can you explain this answer?

Shivam Sharma answered
Working Principle of Photodiodes. When photons of energy greater than 1.1 eV hit the diode, electron-hole pairs are created. The intensity of photon absorption depends on the energy of photons – the lower the energy of photons, the deeper the absorption is. This process is known as the inner photoelectric effect.

The current drawn by a 220 V dc motor of armature resistance 0.5W and back emf 200V is
  • a)
    40 A
  • b)
    44 A
  • c)
    400 A
  • d)
    440 A
Correct answer is 'A'. Can you explain this answer?

Sanaya Basu answered

Calculation of Current drawn by the DC Motor

- Given parameters:
- Supply voltage (V) = 220 V
- Armature resistance (Ra) = 0.5 Ω
- Back EMF (Eb) = 200 V

- The formula for calculating the current drawn by a DC motor is:
- I = (V - Eb) / Ra
- where I is the current, V is the supply voltage, Eb is the back EMF, and Ra is the armature resistance

- Substituting the given values into the formula:
- I = (220 V - 200 V) / 0.5 Ω
- I = 20 V / 0.5 Ω
- I = 40 A

Therefore, the current drawn by the 220 V DC motor with an armature resistance of 0.5 Ω and a back EMF of 200 V is 40 A.

Which meter has the highest accuracy?
  • a)
    PMMC
  • b)
    Moving Iron
  • c)
    Moving-coil
  • d)
    Rectifier
Correct answer is option 'C'. Can you explain this answer?

Swati Shah answered
Accuracy of Different Meters
Accuracy is a crucial factor when it comes to measuring instruments, especially in electrical engineering. Let's explore the accuracy of different types of meters listed in the question.

Moving Iron Meter
Moving iron meters are commonly used for measuring AC currents. They have a moderate level of accuracy but are not as accurate as some other types of meters. They are suitable for general measurement purposes but may not provide the highest level of precision.

Rectifier Meter
Rectifier meters are often used for measuring DC currents. They offer good accuracy but may not be as precise as other types of meters available. They are reliable for many applications but may not be the best choice when high accuracy is required.

PMMC Meter
Permanent Magnet Moving Coil (PMMC) meters are known for their high accuracy. They are often used in precision measurement applications where accuracy is paramount. PMMC meters are sensitive and provide reliable measurements, making them suitable for tasks that require precise readings.

Moving-coil Meter
Moving-coil meters are commonly used for measuring both AC and DC currents. They offer good accuracy and are suitable for a wide range of applications. While they may not provide the highest level of precision compared to PMMC meters, they are still a reliable choice for many measurement tasks.
In conclusion, among the meters listed, the Moving-coil meter has the highest accuracy. However, the choice of meter ultimately depends on the specific requirements of the measurement task at hand.

Two alternators are running in parallel. If the field of one of the alternator is adjusted, it will
  • a)
    reduce its speed
  • b)
    change its load
  • c)
    change its power factor
  • d)
    change its frequency
Correct answer is option 'C'. Can you explain this answer?

Aisha Gupta answered
If the field excitation (voltage adjustment control)of one of a pair of paralleled alternators is turned down, two things will happen: first, the generator in question will develop a less lagging power factor, while the other generator will develop a more lagging power factor, with the overall power factor of the plant and load remaining the same; second, bus voltage, and by extension grid voltage, will drop slightly, unless the other generator’s voltage adjustment (field excitation) is increased proportionally, which will also result in the second generator develop an even more lagging power factor as the first generator’s power factor becomes less lagging.

A power plant has a maximum demand of 15 MW. The load factor is 50% and the plant factoris 40%. The operating reserve is
  • a)
    3 MW
  • b)
    3.75 MW
  • c)
    6 MW
  • d)
    7.5 MW
Correct answer is option 'B'. Can you explain this answer?

Tanvi Shah answered
Load factor is the ratio of average load and maximum load and plant factor is the ratio of average load and plant capacity. Here average load will be 7.5KW and plant capacity will be 18.75KW so reserve will be 3.75KW

The phase difference between the primary & secondary voltage of a transformer is
  • a)
  • b)
    90º
  • c)
    180º
  • d)
    between 30º & 60º
Correct answer is option 'C'. Can you explain this answer?

Amar Sengupta answered
Transformer Phase Difference

The phase difference between the primary and secondary voltage of a transformer is determined by the transformer's construction and the way it is connected.

Explanation:

A transformer is an electrical device that is used to transfer electrical energy from one circuit to another. It works on the principle of electromagnetic induction, which states that when a magnetic field changes in strength or direction, an electromotive force (EMF) is induced in a nearby conductor.

When an AC voltage is applied to the primary winding of a transformer, it creates a changing magnetic field inside the core. This magnetic field induces a voltage in the secondary winding, which is connected to a load. The voltage induced in the secondary winding is proportional to the turns ratio of the transformer.

The phase difference between the primary and secondary voltage of a transformer is determined by the relative position of the windings and the way they are connected. In general, the phase difference between the primary and secondary voltage is 180 degrees.

When the primary voltage is at its maximum, the secondary voltage is at its minimum, and vice versa. This means that the primary and secondary voltages are out of phase by 180 degrees.

However, in some cases, the phase difference between the primary and secondary voltage can be between 30 and 60 degrees. This can happen if the windings are not perfectly aligned or if there is a phase shift in the load.

Conclusion:

In conclusion, the phase difference between the primary and secondary voltage of a transformer is generally 180 degrees. However, it can be between 30 and 60 degrees in some cases. The phase difference is determined by the transformer's construction and the way it is connected.

When diameter of the core and cable is doubled the value of capacitance
  • a)
    will be reduced to one fourth
  • b)
    will be reduced to half
  • c)
    will be doubled
  • d)
    will become four times
Correct answer is option 'A'. Can you explain this answer?

Explanation:
Capacitance is defined as the ability of a system to store an electric charge. It depends on the geometric properties of the system, such as the distance between the two conductors and the area of the conductors.

When the diameter of the core and cable is doubled, the following changes occur:

1. Distance between the conductors: The distance between the two conductors is increased by a factor of 2. This is because the diameter of the core and cable has been doubled, and the conductors are located at the center of the core and cable.

2. Area of the conductors: The area of the conductors is increased by a factor of 4. This is because the area of a circle is proportional to the square of its diameter.

As a result of the above changes, the capacitance of the system is reduced to one-fourth of its original value. This is because capacitance is inversely proportional to the distance between the conductors and directly proportional to the area of the conductors.

Mathematically, the capacitance of a system is given by the formula:

C = εA/d

where C is the capacitance, ε is the permittivity of the medium between the conductors, A is the area of the conductors, and d is the distance between the conductors.

When the diameter of the core and cable is doubled, the value of A is increased by a factor of 4, and the value of d is increased by a factor of 2. Therefore, the capacitance is reduced by a factor of (1/4) x (1/2) = 1/8 or one-fourth.

Chapter doubts & questions for Electrical Engineering (EE) Technical Tests: SSC JE - Mock Test Series for SSC JE Electrical Engineering 2026 2025 is part of Electrical Engineering (EE) exam preparation. The chapters have been prepared according to the Electrical Engineering (EE) exam syllabus. The Chapter doubts & questions, notes, tests & MCQs are made for Electrical Engineering (EE) 2025 Exam. Find important definitions, questions, notes, meanings, examples, exercises, MCQs and online tests here.

Chapter doubts & questions of Electrical Engineering (EE) Technical Tests: SSC JE - Mock Test Series for SSC JE Electrical Engineering 2026 in English & Hindi are available as part of Electrical Engineering (EE) exam. Download more important topics, notes, lectures and mock test series for Electrical Engineering (EE) Exam by signing up for free.